The t-stat will not turn the blower on for the heat I can hear it trying to turn on. On the furnace itself there is a switch that says auto or on I can flip it to the on position and the blower came on heat worked good now there is no heat coming out blower still works when switch is turned to the on position any suggestions of where to start looking for the problem
Hi,
Probably one or both sequencers are bad.
Sequencer # 621383 and Sequencer # 01 - 0840
Both can be seen and ordered through PayPal from this page :
http://www.mobilehomerepair.com/NordyneElec.html
Thanks,
Robert
Probably one or both sequencers are bad.
Sequencer # 621383 and Sequencer # 01 - 0840
Both can be seen and ordered through PayPal from this page :
http://www.mobilehomerepair.com/NordyneElec.html
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 0 Replies
- 68693 Views
-
Last post by newguy47
Thu Aug 16, 2018 8:21 pm
-
-
heater blower intertherm feh-015ha-03
by newguy47 » Wed Oct 24, 2018 8:04 am » in Nordyne Service & Repair - 0 Replies
- 75062 Views
-
Last post by newguy47
Wed Oct 24, 2018 8:04 am
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 143774 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
intertherm feh-015ha-04 Noisy Blower
by kjaxes99 » Sat Oct 24, 2020 4:45 am » in Nordyne Service & Repair - 0 Replies
- 126318 Views
-
Last post by kjaxes99
Sat Oct 24, 2020 4:45 am
-
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 55962 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-