E1EB-015HA Electric Furnace Issue

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Mark, Greg

Locked
RipBeak
Posts: 2
Joined: Mon Nov 14, 2011 6:26 pm

Mon Nov 14, 2011 6:35 pm

I have a E1EB-015HA Electric Furnace that will not blow air. I can see the elements heart up (glowing hot) but the blower will not kick on. I've verified breakers are working and no damaged or loose wires to anything inside. Oddly the elements will heat for about 30 seconds before the limiter kick them off no matter what even with the thermostat is sent to cool or I switch the blower from auto to on but no blower. Thinking it's with a Sequencer or Contractor any thoughts?


User avatar
Mark
Site Admin
Posts: 742
Joined: Sat Feb 17, 2007 4:23 pm
Location: Aberdeen, SD
Contact:

Thu Nov 17, 2011 12:11 pm

The blower needs to come on at the same time that the elements do. Possible culprits are the blower relay part # 621867R http://www.aberdeenhomerepair.com/store ... ay-01-0157

and the 01-0840 sequencer http://www.aberdeenhomerepair.com/store ... 8621696%29

Mark
You can't fail if you don't try!

RipBeak
Posts: 2
Joined: Mon Nov 14, 2011 6:26 pm

Fri Dec 02, 2011 1:35 pm

Okay I replaced the two parts suggested, blower relay part # 621867R and the 01-0840 sequencer,
and the furnace still will not work but the symptoms have slightly changed.

I still cannot get the blower to kick on no matter what I do but now the thermostat doesn't appear to have any effect on the furnace. If I put the fan switch in auto the furnace is lifeless but if I put the switch to on the elements heat up until the limiter kicks in.

I have verified all wires are tightly connected and voltage appears fine. Would either the 621383 Sequencer or the Transformer cause such an issue to occur?

Thanks for your help and suggestion

Locked