Our Coleman furnace is in the middle of our double-wide, and heat comes out great from the middle of the MH, all the way to the back bedrooms.
Our problem is the living room, on the other end of the house.
The air that's coming out is lukewarm, at best. It's never been particularly warm, but it's especially noticeable since these blasts of arctic air have been bringing temps near zero, or below.
Any ideas of what could be causing this? Any help is appreciated.
My unit's fine - Am asking about the ducts
Hi,
Holes and/or separations in main ducts or in the crossover duct beneath home IF this room is on opposite side of home from furnace.
Remove registers and use flashlight and mirror to inspect ducts from above. Lay light down in duct and go to next register and look back toward light with a mirror.
OR, lay a good digital camera with flash in duct and take some pics, put them on computer and enlarge for good look see at duct.
Thanks,
Robert
Holes and/or separations in main ducts or in the crossover duct beneath home IF this room is on opposite side of home from furnace.
Remove registers and use flashlight and mirror to inspect ducts from above. Lay light down in duct and go to next register and look back toward light with a mirror.
OR, lay a good digital camera with flash in duct and take some pics, put them on computer and enlarge for good look see at duct.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Posts: 622
- Joined: Tue Nov 11, 2008 6:12 pm
- Location: wisconsin
I used a digital camera to check out my ducts this past summer and it works great. Have to get it lined up just right so it can take a couple shots to see what you want.
-
- Similar Topics
- Replies
- Views
- Last post
-
- 1 Replies
- 30155 Views
-
Last post by Greg
Fri Apr 20, 2018 5:11 pm
-
- 2 Replies
- 45421 Views
-
Last post by Mark440
Thu Apr 11, 2019 11:15 am
-
- 3 Replies
- 25560 Views
-
Last post by mackendw
Sat Jan 11, 2020 8:49 am
-
-
Ducts barely blowing - what to check first?
by caligirl » Fri Nov 25, 2022 1:21 pm » in All Other HVAC Questions - 0 Replies
- 90123 Views
-
Last post by caligirl
Fri Nov 25, 2022 1:21 pm
-
-
-
G.E.supplemental coil heater in wall unit
by stevenbrooks » Mon Jul 17, 2017 4:00 pm » in Service & Repair of Other Brands - 0 Replies
- 29693 Views
-
Last post by stevenbrooks
Mon Jul 17, 2017 4:00 pm
-