anticipator settings?

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
bobbyjoes

Hello, I have a old coleman presidential 2 furnace, could you tell me what the anticipator settings are for heat ,it runs short cycles,thanks,Model #77008,series 856
User avatar
hvac1000
Posts: 292
Joined: Wed Feb 28, 2007 9:19 am
Location: Cincinnati ohio

There are no magic settings because it takes the current draw of the gas valve and all the other circuits on the heat side of the system to set it absolutely correct and this varies with the install, length of thermostat wire, gas valve current ETC to set the anticipator. I always use a Amprobe. to set it up correctly.

Now you can slide the heat anticipator lever to longer or + to make the run time longer. Do it just a little bit at a time until you hit the correct spot
God, grant me the serenity
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Look on the gas valve for a good starting point.

Halfway between .4 and .5 is design point.

It can need adjusting though as HVAC stated.