Burner and Pilot goes out after 15 mins.

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
Darren
Posts: 2
Joined: Mon Dec 27, 2010 9:22 pm

I have a Coleman Evcon Presidential model#7975C856. I can light the pilot and it stays lit. Strong blue flame. I push the thermostat up and the unit comes on.Burner has a strong blue flame and the fan kicks in like it is suppose to do. But after 15-20 mins., the flame goes out and the pilot goes out. What could be the culprit?

Thanks,
Darren
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Bad gas valve possibly. Would need to thoroughly test it to know for sure.

Do you have 24vac at gas valve when all goes out ?



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Darren
Posts: 2
Joined: Mon Dec 27, 2010 9:22 pm

Yes I do have a 24vac gas valve. What is the best way to test it???
By the way, thanks for the super quick response!!
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

When the burner and pilot go out, do you have 24vac at the gas valve terminals ?


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?