I have a Nordyne MIMC 090A. The electronic ignitor is new and it will initially light, sense the flame, but then the flame goes out. Sometimes the flame kicks on and off several times before it stays lit. Combustion Blower Assembly has also been replaced.
it has a combination ignitor/flame sensor. It has been replaced, and it is sensing the flame, then the lp gas kicks off, then on, then off several times until it stays lit, or the gas kicks off and it runs through the cycle again with the ignitor coming on.
Check your ground wires. They usually are green but they can be almost any color. The situation you have is intermittent and a loose/corroded connection will cause this.
Now for my stupid question. Are you sure you have gas? I just had to toss that one in.
Now for my stupid question. Are you sure you have gas? I just had to toss that one in.
God, grant me the serenity
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
Also check roof-jack assembly from furnace all the way up.
Make sure it is clear and not damaged or seperated anywhere.
Thanks,
Robert
Make sure it is clear and not damaged or seperated anywhere.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Yes, propane tank is 60% full. Checked grounds, and nothing seems to be loose and they are nice and shiney (no corrosion).
Roof jack is fine. any other suggestions? Could the gas valve be bad or something like that?
Hi,
Yes, but you first rule out the smaller and more common things that also cost less.
See if GV maintains 24vac power at all times.
If so, would need proper tools/equipment to see if gas pressure was correct to burner.
Has any work been done on it lately or any changes ?
Thanks,
Robert
Yes, but you first rule out the smaller and more common things that also cost less.
See if GV maintains 24vac power at all times.
If so, would need proper tools/equipment to see if gas pressure was correct to burner.
Has any work been done on it lately or any changes ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Colman evcon presidental 7980B856 furnace will not stay on
by ezridersid » Sat Dec 21, 2019 8:52 pm » in Mobile Home Repair - 1 Replies
- 17188 Views
-
Last post by ezridersid
Sat Dec 21, 2019 9:04 pm
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167216 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne M1B1 furnace issue - thermostat c wire not hooked up correctly. It's running off atteries instead
by Tallestt » Mon Apr 20, 2020 6:27 am » in Nordyne Service & Repair - 1 Replies
- 43099 Views
-
Last post by taurolyon
Tue Jun 23, 2020 4:02 pm
-
-
- 2 Replies
- 27240 Views
-
Last post by plumducky
Tue Dec 10, 2019 3:59 pm
-
- 0 Replies
- 32465 Views
-
Last post by clsmatHH
Wed Oct 16, 2019 12:43 pm