Dgaa070dbta - lights, indicator normal, lukewarm air
Indicator is solid, strong flame, fan starts up, good airflow at both ends of house (it's located dead center of house) but only blows room temperature air. Last night when it said 65 I set it to 71 and woke up to 60. This afternoon jumped it all the way to 77 and its hovered around 63-65 depending on how many candles I've got going to keep it warm in here.
If you are sure about the burner flame being correct, you may have a bad baffle in the heat exchanger. Pull the burner assembly and reach up in the heat exchanger to be sure the baffle is still in place. It is located about 16" above the burner assembly opening. It should be tight in place in there. I have seen some where the rivets holding them rust away and the baffle falls or tilts. This allows too much heat to escape out of the heat exchanger and you end up short changed on heat as most of it goes out the roof jack.
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Upflow vs Downflow Air: Seeking Opinions
by rockncountry101 » Tue May 30, 2017 8:37 am » in Mobile Home Repair - 4 Replies
- 23190 Views
-
Last post by Mark440
Tue Jun 20, 2017 1:12 pm
-
-
-
DGAT Series furnace air-conditioning issue
by minnie1967 » Thu Jul 13, 2017 9:48 am » in Coleman Service & Repair - 0 Replies
- 56780 Views
-
Last post by minnie1967
Thu Jul 13, 2017 9:48 am
-
-
-
Disable Blend Air ll Attic fan
by 777stickman » Fri Nov 17, 2017 5:05 pm » in Coleman Service & Repair - 0 Replies
- 41616 Views
-
Last post by 777stickman
Fri Nov 17, 2017 5:05 pm
-
-
- 1 Replies
- 22036 Views
-
Last post by Greg
Tue Dec 26, 2017 7:33 pm
-
- 0 Replies
- 31156 Views
-
Last post by Elainesplay
Sat Jul 13, 2019 9:54 am