Hi there, I tried to do as much of my own research as possible before posting this to refrain from posting yet another "oh no its broke" topic.
I have a Coleman Evcon DGAT070BDC furnace/ac that is failing to properly ignite the burner, at least from what I can tell. During its sequence the Thermostat calls for heat, the draft fan starts up, few seconds later the Hot Surface Ignition fires up and stays red for about 10 seconds or more, then the HSI shuts off. The furnace tries this indefinitely I believe.
I am at the point now where I am out of guesses, I don't actually see the burner fire up then shut off so I am unsure if the flame sensor is to blame or what is happening. Any ideas?
Coleman Evcon, Furnace won't Ignite
You could always clean the flame sensor with a bit of steel wool. But if it's not even lighting, then check and see if you are getting power to the gas valve during that period of the start-up. If you are getting power, perhaps the gas valve isn't opening and you need a new valve. If you aren't getting power, then look for a faulty limit switch.
Mark
Mark
You can't fail if you don't try!
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Colman evcon presidental 7980B856 furnace will not stay on
by ezridersid » Sat Dec 21, 2019 8:52 pm » in Mobile Home Repair - 1 Replies
- 16567 Views
-
Last post by ezridersid
Sat Dec 21, 2019 9:04 pm
-
-
- 0 Replies
- 106776 Views
-
Last post by cwwhite75
Sat Feb 29, 2020 8:46 am
-
- 2 Replies
- 19446 Views
-
Last post by TorstenW
Tue Mar 06, 2018 1:04 am
-
-
Intertherm FEH-017HAC won't shut off
by Jetherid » Mon Dec 07, 2020 6:22 pm » in Nordyne Service & Repair - 0 Replies
- 168893 Views
-
Last post by Jetherid
Mon Dec 07, 2020 6:22 pm
-
-
-
Transformer burning out in an Evcon DES 80
by BigDave67s » Wed Dec 29, 2021 10:01 pm » in Coleman Service & Repair - 0 Replies
- 108572 Views
-
Last post by BigDave67s
Wed Dec 29, 2021 10:01 pm
-