miller gas furnace model#G5RK060C-12-H

Posted: Fri Jan 14, 2011 1:44 pm
by scar
hi,this is my problem.the furnace is running ok,but, if i set the thermostat to a lower temp.,when the temp in house drops to new setting and below,the furnace won't start,and i get 4 flashes on red light on furnace panel ,that says ignition failure,if i then lower thermostat setting and then increase temp. setting,furnace will start,and work ok.

Re: miller gas furnace model#G5RK060C-12-H

Posted: Sat Jan 15, 2011 3:29 am
by Robert
Hi,

Possibly a bad thermostat. Does t-stat click and furnace does not come on or does the t-stat do nothing as well ?



Thanks,
Robert

Re: miller gas furnace model#G5RK060C-12-H

Posted: Sun Jan 16, 2011 10:10 pm
by scar
thanks robert,i found the flame sensor carboned up some,took some embry cloth and cleaned it up and everything seems to be working ok now.

Re: miller gas furnace model#G5RK060C-12-H

Posted: Mon Jan 17, 2011 11:51 pm
by Robert
Hi,

It may stay ok, but often they don't. Shouldn't use emery cloth on them. Use steel wool and gently clean til all the carbon is gone.


The emery cloth will leave a residue that is harmful to the sensor rod.


Thanks,