Nordyne Intertherm M1MB 056A BW won't light

Posted: Sat Dec 25, 2010 6:56 pm
by kiko88
Status light is red b4 I try to turn on the heater. Call for heat, the draft inducer motor turns on, the ignitor glows orange and after a couple of minutes nothing happens and then shuts down with no status indicators after that. Have 24v at the transformer. Have gas at the gas valve. Have 115v at the ignitor plug and voltage at the gas valve. The limit switches are closed before I turn on the heater. Once in a while it works just fine. Could it be a bad board or gas valve? How do I check the board or gas valve? Any ideas anyone.....

Re: Nordyne Intertherm M1MB 056A BW won't light

Posted: Sat Dec 25, 2010 7:35 pm
by Robert
Make sure the burner orifice/spud and burner tube are clear and not clogged (spider-web-bugs).

IF all is clear, ignitor is glowing and you have 24vac at gas valve, then I would suspect the gas valve.


Would need an hvac tech to test the manifold pressure to see if it is working correctly.

IF it gets the 24vac and maintains it, then the gas should flow.



Thanks,
Robert

Re: Nordyne Intertherm M1MB 056A BW won't light

Posted: Thu Jan 06, 2011 9:14 am
by kiko88
The problem was the board was giving me 12v at the gas valve. Will have to replace the board. Sometimes it gives the 24v needed to start the gas valve. Weird. Faulty board

Re: Nordyne Intertherm M1MB 056A BW won't light

Posted: Thu Jan 06, 2011 3:20 pm
by Robert
Hi,

That happens sometimes. Can give ordering info if needed. Or, you can call Mark @ 605-229-2627 and see about getting it looked at and maybe repaired.


Thanks,