Nordyne Furnace -Locking out on failed ignition

Posted: Sun Dec 12, 2010 5:09 pm
by darkdw15
I have a Nordyne Intertherm Furnace, Model number M1MB 070A AW, the furnace locks out due to failed ignition, but it only does it very rarely but when it is burning the warning light is flashing for weak flame.

I have checked the pipes and there is no blockage also the ignitor works, so it has air, fuel and the ignitor is working, what else would be needed to have a srong flame??

When it locks outsI just turn it on and off and it lights every time,

Naturally being winter this could cause some seriuos problems when I am at work,

Any help to what the problem might be would be very helpful,

Thanks

Donny

Re: Nordyne Furnace -Locking out on failed ignition

Posted: Mon Dec 13, 2010 4:59 pm
by gordo48111
Make sure the burner tube and burner orifice/spud are clear with no obstructions.

Check behind orifice/spud for spider/web/bugs.

Re: Nordyne Furnace -Locking out on failed ignition

Posted: Tue Dec 14, 2010 10:00 pm
by Robert
Failed ignition is usually bad ignitor, remote flame sensor or gas valve.

Do you get 120vac to ignitor for about 30 secs. or so ?


Thanks,
Robert

Re: Nordyne Furnace -Locking out on failed ignition

Posted: Wed Dec 15, 2010 11:46 am
by darkdw15
Thanks for the tips,

I went to check the orifice and found that the wrong orifice was in the furnace and the pressure regulator was also wrong, the gas valve & orifice were setup for propane,

So I switched it all around and all is workign as it should be, that is how is was when I bought it, seems like somethign that you shouldn't have to check,

Thanks Again for the help,

Re: Nordyne Furnace -Locking out on failed ignition

Posted: Wed Dec 15, 2010 2:48 pm
by Robert
You're very welcome, happy to help.

Never rule out anything before checking.


Thanks,