Coleman Evcon DGAT075BDD blinking 5 times
This has been going on for almost 2 years now. I know that the code is "gas valve energized with no call for heat". I'm tired of the fan coming on and blowing cool air when the temp is above what the thermostat is set at. So every time this happens (which is a lot) I go to the furnace and turn the power switch off until the temp gets down to where the furnace will kick on. Then the furnace will work fine for sometimes a few days with no problems.The board has been replaced 3 times and the last time was about a year ago. Should I try to change the gas valve? If you could let me know the part number that I need it would be appreciated. Thanks.
-
- Posts: 67
- Joined: Fri Nov 12, 2010 10:45 am
The gas valve is not the problem. It is energized by 24V across its terminals which would normally come from the thermostat. If it is energized with no call for heat from the thermostat (this is what the error code means), the valve is being powered from somewhere other than the thermostat - most likely from the board itself. I have read several posts on this site about people having to replace boards every year or two. In my 25+ years in the HVAC/R field, this is not the norm. Voltage spikes can contribute to premature failure of a board and I recommend the control circuit be fused, if it is not already.
"Man...that blowed up real good!"
Test the gas valve for 24vac.
IF you have it, test board across W and C for 24vac.
Then trace wires from GV to board, unplug the connector and test across board corresponding holes/pins for 24vac that connect to GV wires.
Thanks,
Robert
IF you have it, test board across W and C for 24vac.
Then trace wires from GV to board, unplug the connector and test across board corresponding holes/pins for 24vac that connect to GV wires.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 47511 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-
-
- 0 Replies
- 109894 Views
-
Last post by cwwhite75
Sat Feb 29, 2020 8:46 am
-
-
Colman evcon presidental 7980B856 furnace will not stay on
by ezridersid » Sat Dec 21, 2019 8:52 pm » in Mobile Home Repair - 1 Replies
- 17250 Views
-
Last post by ezridersid
Sat Dec 21, 2019 9:04 pm
-
-
-
Transformer burning out in an Evcon DES 80
by BigDave67s » Wed Dec 29, 2021 10:01 pm » in Coleman Service & Repair - 0 Replies
- 111824 Views
-
Last post by BigDave67s
Wed Dec 29, 2021 10:01 pm
-
-
-
Evcon Heat Pump - Air Conditioner Model No. BRHS036B Making HUM Before Starting
by Dave_L » Tue Aug 29, 2023 1:26 am » in Coleman Service & Repair - 0 Replies
- 126313 Views
-
Last post by Dave_L
Tue Aug 29, 2023 1:26 am
-