Intertherm Sometimes Won't Restart

Posted: Thu Nov 18, 2010 1:55 pm
by afranch
For much of the time the unit works fine.

What happens is occaisionally after the thermostat shuts the furnace down, the furnace won't restart.The furnace is clearly is getting the signal to restart because I can hear a repeated clicking noise as the unit tries to switch itself on.

What is that clicking noise and what will I need to do to fix the furnace?

Thanks in advance!
Andy

Re: Intertherm Sometimes Won't Restart

Posted: Fri Nov 19, 2010 4:58 am
by Robert
Hi Andy,

What is the furnace model number ?



Thanks,
Robert

Re: Intertherm Sometimes Won't Restart

Posted: Sat Nov 20, 2010 10:25 am
by afranch
Hey Robert, thanks for getting back so quickly. It's an FEH-015HA.

Re: Intertherm Sometimes Won't Restart

Posted: Sat Nov 20, 2010 9:30 pm
by Robert
Hi Andy,

Most likely a bad sequencer.


Sequencer # 901075 can be seen and ordered here by paging down :

http://www.aberdeenhomerepair.com/store ... esults.php



Thanks,
Robert

Re: Intertherm Sometimes Won't Restart

Posted: Mon Nov 22, 2010 5:11 pm
by afranch
A little more info I got (this is not in my home) is that the thermostat is what was doing the clicking. The furnace wasn't doing anything except perhaps a low hum.

The failure to restart is something that might happen once a week. I just replaced the thermostat and ran new wire and we are going to see if that handles it.

Do you still think it's a bad sequencer Robert?

Re: Intertherm Sometimes Won't Restart

Posted: Tue Nov 23, 2010 1:20 am
by Robert
Hi,

Depends on clicking and how many and where sound came from. T-Stat may be problem, but most often a sequencer.



Thanks,
Robert

Re: Intertherm Sometimes Won't Restart

Posted: Thu Dec 30, 2010 3:41 pm
by afranch
Hi Robert,

The new thermostat did not help and I am going to try ordering and installing a sequencer. Before I do, is replacing a sequencer a very complicated repair? Will I need a manual or a wiring diagram? I've wired boxes, fixtures, outlets, switches, thermostat/furnace, etc.....how does this repair compare in terms of complexity?

Re: Intertherm Sometimes Won't Restart

Posted: Thu Dec 30, 2010 3:52 pm
by afranch
Whoops, now I see there's an instruction sheet where I order the part!

Looks like something I can handle, but would like your opinion on difficulty. Does the furnace need to be removed to install the sequencer?

Re: Intertherm Sometimes Won't Restart

Posted: Thu Dec 30, 2010 4:36 pm
by Robert
Turn power OFF, mark each wire or write where they go, Taking digi pics or video before is good.

Not very hard at all, just be sure each wire goes to correct terminal.


Thanks,
Robert

Re: Intertherm Sometimes Won't Restart

Posted: Thu Jan 06, 2011 11:35 am
by afranch
One more thing Robert....this is in a tenant's mobile home and I am trying to figure out how long it will take to do the repair.

Would I have to pull the whole furnace? Are the places I need to wire easy to access? I am going to check Nordyne's website and see if I can pull an old manual on this furnace.

Thanks!
Andy

Re: Intertherm Sometimes Won't Restart

Posted: Thu Jan 06, 2011 3:30 pm
by Robert
Hi Andy,

Remove lower door panel, remove bottom controls cover panel from lower left opposite the fuses or breakers.


Sequencer is on back wall down inside there. Kinda cramped and wires in the way, most go to sequencer.

Male prong in one corner, one screw in opposite corner holds it in place.


That and the wires is all there is.

Top and middle spades are M1 thru M8. (120vac)

Very bottom are H1 thru H4, coil terminals. (24vac).

Be sure power is OFF to furnace. Flip furnace breaker at service panel and also the breakers at the furnace or pull the fuses.


Turn t-stat OFF.

30 minutes to 3 hours depending on eyes, reach and flexibility.


Thanks,
Robert