I have an Intertherm FEH-015HA where the HEAT works perfectly when t-stat set to auto and fan/blower set to auto. However, the A/C will only kick on and stay on when the fan/blower is set to the ON position. I've read multiple posts about the opposite problem where the A/C works and it's the heat that has issues, but have yet to see any posts on this. If anybody could direct me to any forum post regarding this issue or just shed some light on the issue I'd greatly appreciate it. I replaced the t-stat, thought maybe the 1986 model DUOTHERM I had was bad, but same issue with the Honeywell, so now I have to troubleshoot the actual unit. Fuses are all good...just don't know where to go from here. Thanks in advance!
DP
Intertherm FEH-015HA fan not starting-A/C
Hi,
1- When you say a/c won't kick on in auto, is it the outside a/c condenser only not coming on or that and the inside furnace blower also ? One or both ?
2- How many wires are connected to the t-stat ? Two or four/five ?
Thanks,
Robert
1- When you say a/c won't kick on in auto, is it the outside a/c condenser only not coming on or that and the inside furnace blower also ? One or both ?
2- How many wires are connected to the t-stat ? Two or four/five ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
The outside unit kicks on but the inside fan/blower doesn't kick on. I have 4 wires connected to the t-stat. I have yellow to Y, green to G, red to RC, and white to W. Those are the only 4 hooked up. I hooked it up exactly how the other stat was hooked up.
Sounds like either a stuck fan relay or a wiring problem in the cooling circuit.
When the t-stat calls for cooling, 24vac should go through the green t-stat wire to fan relay coil (1 and 3). That should energize the coil, open contacts 5 and 6 and close contacts 2 and 4 sending 120vac to motor for cooling high speed 1 leg.
Other 120vac leg comes from fuse.
Thanks,
Robert
When the t-stat calls for cooling, 24vac should go through the green t-stat wire to fan relay coil (1 and 3). That should energize the coil, open contacts 5 and 6 and close contacts 2 and 4 sending 120vac to motor for cooling high speed 1 leg.
Other 120vac leg comes from fuse.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 157818 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
- 0 Replies
- 74176 Views
-
Last post by newguy47
Thu Aug 16, 2018 8:21 pm
-
-
heater blower intertherm feh-015ha-03
by newguy47 » Wed Oct 24, 2018 8:04 am » in Nordyne Service & Repair - 0 Replies
- 80485 Views
-
Last post by newguy47
Wed Oct 24, 2018 8:04 am
-
-
-
intertherm feh-015ha-04 Noisy Blower
by kjaxes99 » Sat Oct 24, 2020 4:45 am » in Nordyne Service & Repair - 0 Replies
- 134753 Views
-
Last post by kjaxes99
Sat Oct 24, 2020 4:45 am
-
-
-
Intertherm FEH-017HAC won't shut off
by Jetherid » Mon Dec 07, 2020 6:22 pm » in Nordyne Service & Repair - 0 Replies
- 164826 Views
-
Last post by Jetherid
Mon Dec 07, 2020 6:22 pm
-