intertherm furnance not shutting down

Posted: Tue Mar 17, 2009 6:58 pm
by turkee56
i have a intertherm furnace model feh-017h. the problem here is it keeps blowing fuses or are burnt.the furnace keeps running and won't shut down using the thermostat. a repair guy came over and said it is the sequencers .this model has two on a metal plate.
i don't have manual and i don't know which ones to buy. i called a furnace parts and said , need part number off of sequencers. this a 1981 furnance and my stepson doesn't want to buy a new furnace.
another forum says its the heat kit that causes to blow fuses.any help on this and does anyone have a part number for the sequencers or do you think its the heat kit.
thanks.

RE: intertherm furnance not shutting down

Posted: Tue Mar 17, 2009 11:22 pm
by Robert
Hi,

Could be just the sequencer or could be both. Would have to test voltages and amp draw to know for sure.


Sequencer most likely keeping it running. That fault or a bad disconnect assembly could be causing fuses to blow.


Sequencer # 901075


Disconnect Assembly # 621029


Either or both can be seen and ordered through PayPal from

this page here :

http://www.mobilehomerepair.com/NordyneElec.html


A reputable hvac tech could diagnose and tell you for sure.



Thanks,
Robert

Re: intertherm furnance not shutting down

Posted: Sat Jan 02, 2010 11:17 am
by brandn
Model# FEH-010H..... When u turn the breaker off and turn the furnace on auto mode it will not turn back on, but if it the furnace on mode and turn the breaker on it comes on.....

Re: intertherm furnance not shutting down

Posted: Mon Jan 04, 2010 11:49 am
by Robert
Hi,

Please start a new thread with your question to keep confusion down,

Then come back here and delete the post here.



Thanks,
Robert