foul odor from a/c vents

Posted: Tue Sep 02, 2008 1:46 pm
by ccox0915
I have been experiencing a foul odor (rotten egg) smell which occasionally comes from the air conditioning vents. It does not occur when using the heater, only the a/c. The gas company came out and confirmed that it was not caused by natural gas. Any ideas?

RE: foul odor from a/c vents

Posted: Wed Sep 03, 2008 2:19 am
by Robert
Hi,

Could be from bacteria/mold/mildew on a-coil being crried through ducts.

Could be from something underneath home and the odor getting into the duct.


Have a-coil and drainline/drain pan cleaned thoroughly and inspect the duct trunkline(s).


Remove registers and lay flashilight down in duct, go to next register and hold mirror down in duct and look back toward light. repeat throughout home to inspect the trunkline(s).


If in a double or triple wide, go under and ensure cross over ducts are not opened anywhere.


Also inspect underneath home for any moldy/smelly areas or excessive wetness.


Take care and best wishes,
Robert