Hi, E2Eh-015HA heat unit, and DRHQ0421CD outside.
The thermostat unit red light flashes twice and the fan blows almost constantly, but the outside unit will not kick in. I cleaned everything,replaced the filter and reset all breakers. when I restart the fan comes on and in a few minutes the outside compressor kicks in as normal. when it gets to temp and shuts off, the red light comes back on and the same thing happens again. emergency heat works fine.
Thanks in advance!
Heat pump not kickin in(heating problem)
First thing to check is the contactor in outdoor heat pump condenser unit to see if it is energizing, pulling in and holding to allow power to unit.
When they start going bad, they will work intermittantly.
Thanks,
Robert
When they start going bad, they will work intermittantly.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
OK, Just went ahead and replaced the contactor. unit powered up,ran to temp. When it kicked in again the outside unit powered up and ran for a minute or two. It then kicked off but the red light is now blinking twice and the fan is running constantly as before.
Just a side note....the paper that came with the unit says the red light code means clean the filter, but that doesnt make sense, I have had this thing apart and cleaned everything??
stumped
Just a side note....the paper that came with the unit says the red light code means clean the filter, but that doesnt make sense, I have had this thing apart and cleaned everything??
stumped
May not be filter, but still be an airflow problem and fall under the filter criterior.
Due to special circumstances involved with heat pumps, I would call a hvac tech out to look at it.
Thanks for inquiring,
Robert
Due to special circumstances involved with heat pumps, I would call a hvac tech out to look at it.
Thanks for inquiring,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 0 Replies
- 39620 Views
-
Last post by David DeBord
Sun Oct 22, 2017 7:13 am
-
-
have intertherm heat pump with a 913421 control box tying to a miller 841 thermo stat ,
by hillcat01 » Mon Oct 21, 2019 7:28 pm » in Nordyne Service & Repair - 0 Replies
- 83022 Views
-
Last post by hillcat01
Mon Oct 21, 2019 7:28 pm
-
-
-
Evcon Heat Pump - Air Conditioner Model No. BRHS036B Making HUM Before Starting
by Dave_L » Tue Aug 29, 2023 1:26 am » in Coleman Service & Repair - 0 Replies
- 118805 Views
-
Last post by Dave_L
Tue Aug 29, 2023 1:26 am
-
-
- 2 Replies
- 24719 Views
-
Last post by plumducky
Tue Dec 10, 2019 3:59 pm
-
- 0 Replies
- 30322 Views
-
Last post by clsmatHH
Wed Oct 16, 2019 12:43 pm