Intertherm model MMHB-090ABHR-06 gas regualtor problems?
Hey y'all, just bought a repo 1997 doublewide, put it on a basement, plummed everything up and the furnace wouldn't work. Draft inducer. Just replaced the draft inducer earlier today, fired the furnace up, it turned the ignitor on, turned the gas on, ignited, turned the ignitor off, five to ten seconds later gas shuts off. Draft inducer doesn't stop running during all of this(it does if I turn the thermostat down) about 30 seconds after the gas shuts off it goes through the whole process again. Same thing. I turned the gas shut-off valve down to where it was closed 3/4 of the way. Ignitor turns on, gas turns on, ignitor turns off, gas stays lit. It stayed lit for as long as I could endure standing around watching and listening(about two hours.) There is no flame sensor on this unit, I looked everywhere, there isn't a spot on the controller for one either. Could the regulator be at fault for this? This is a natural gas furnace, it has natural gas hooked to it now, it had natural gas hooked to it at the park where we got it from. This is a heat and a/c unit. I believe the trailer sat for about 7 months or more with no service turned on. Any help is very appreciated. Frustrated and confused.
Hi,
The ignitor is also the flame sensor. When burner shuts off like that, see if gas valve is still getting 24-28vac at the GV terminals.
If not, then the problem is electrical and/or safety issue.
Most common is the ignitor/flame sensor.
If you need a price quote, let me know.
Take care and best wishes,
Robert
The ignitor is also the flame sensor. When burner shuts off like that, see if gas valve is still getting 24-28vac at the GV terminals.
If not, then the problem is electrical and/or safety issue.
Most common is the ignitor/flame sensor.
If you need a price quote, let me know.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Thanks Robert, that's exactly what was wrong. I failed to mention that I replaced the ignitor, it wasnt exactly a direct fit. After tweaking it just a bit, it was right in the flame path and the furnace was running like new. Thank you, and yes, I would like a price quote for an ignitor, always good to have a spare handy.
Hi,
You're very welcome, happy to help.
Ignitor # 902661A @ $41.85 + $6.75 shipping .
It can be seen and order through Paypal from right side here:
http://www.mobilehomerepair.com/NordyneGas.html
Let me know if outside the U.S. for added ordering info.
Thanks.
Take care and best wishes,
Robert
You're very welcome, happy to help.
Ignitor # 902661A @ $41.85 + $6.75 shipping .
It can be seen and order through Paypal from right side here:
http://www.mobilehomerepair.com/NordyneGas.html
Let me know if outside the U.S. for added ordering info.
Thanks.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 67234 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 107461 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
- 0 Replies
- 42668 Views
-
Last post by chrismc_us
Mon Dec 23, 2019 9:00 am
-
-
2-combo single pole lightswitch problems
by hstassen » Mon Jan 06, 2020 9:41 pm » in Mobile Home Repair - 2 Replies
- 12365 Views
-
Last post by Greg
Tue Jan 07, 2020 6:12 pm
-
-
-
I am thinking of switching to a gas water heater
by deryk the gypsy » Sat Jul 22, 2017 7:16 am » in Mobile Home Repair - 2 Replies
- 34964 Views
-
Last post by Greg
Sat Jul 22, 2017 12:26 pm
-