Stopped blowing hot air last night. Had got to the point it took a while to warm the trailer.
Was thinking I might need new coils.
Intertherm Central Electric Furnace
FEH-012HA
240v
60hz
1 phase
41,000 BTUH
12kw
Any help would be greatly appreciated.
Not a lot of money to spend either.
RE: Intertherm FEH-012HA
Posted: Fri Dec 07, 2007 4:08 am
by Robert
Need to know if sequencer is sending signal to all elements and if so, are they working.
See if bottom H1/H2, H3/H4, etc are getting 24vac from t-stat.
If so, do you have 240vac at M1/M2, M3/M4, etc. ?
Thanks,
Robert
RE: Intertherm FEH-012HA
Posted: Fri Dec 07, 2007 10:27 am
by ncObserver
I've back tracked a little on the coils...
I did a little more trouble shooting last night and found that the NON-40 fuses were both brittle and broke when I removed them.
I have purchased new fuses (both Non-40 and Non-30 which are required) and will replace this evening.
I'm hoping this may be the fix, but I will let you know more later this evening.
RE: Intertherm FEH-012HA
Posted: Fri Dec 07, 2007 6:17 pm
by ncObserver
The fuses did the trick. Sweet heat.
Heat hasn't been this good in a couple of years.
Thanks for you help and I'm glad I found this site.
RE: Intertherm FEH-012HA
Posted: Mon Dec 10, 2007 3:52 am
by Robert
Hi,
You're very welcome, glad it is fixed.
Take care and best wishes,
Robert