Coleman heater gets stuck going off and on...

Posted: Thu Nov 22, 2007 1:02 pm
by crusaderjsj
Coleman Furnace Model 7680B Series 856----Sometimes the furnace seems to get stuck and it keeps going off and on, off and on--especially when it is running at a higher temperature like 70 degrees...at 65 degrees it doesn't seem to happen or doesn't happen as often. Last winter I replaced the fan/limit with part no. S1-7975-3281, but perhaps it is defective. If I turn the furnace off for awhile it will work okay again. I've cleaned the blower fan and opened the registers--could it be the thermostat???

It has two limit switches #7680-379, one is on the front and one is by the blower, would these have anything to do with it--description says they turn off the gas at certain times.

Thanks for your help, Jardy

RE: Coleman heater gets stuck going off and on...

Posted: Thu Nov 22, 2007 7:58 pm
by hvac1000
Sometimes the furnace seems to get stuck and it keeps going off and on, off and on

What is going off and on the blower or the burner?

Posted: Sat Nov 24, 2007 12:58 am
by crusaderjsj
The blower--it goes on for a few seconds and then off for a few seconds and this cycle keeps repeating itself until I turn it off.

Posted: Sat Nov 24, 2007 6:30 am
by hvac1000
If you can put the blower in a constant run position. You can do this by using a jumper on the control you replaced last year. This will take the control out of the circuit and eliminate the on and off if the control is the problem.

If this corrects the situation then you know the control is defective if not we will have to look elsewhere.

Careful with the jumper. You might look at the wiring diagram to be sure of what you are doing.