My furnace is model # 7995-656/D
When the furnace is off there is a constant humming noise.
When I turn the fan switch off it goes away.
The furnace also has very short cycles, and when the cycle ends
after about a minute the blower starts back up for about 45 seconds to a minute. Any help would be appreciated. The anticipator setting is at .2
Thanks, jford

RE: Coleman Presidential Furnace

Posted: Tue Nov 13, 2007 10:13 am
by Robert
You'll have to open control box and try to determine exactly where it is coming from.


Look in your owners manual or on the gas valve itself or on the data sticker on furnace for the correct heat anticipator setting.


Make sure filter is clean and also a-coil if you have a/c.



Thanks,
Robert

RE: Coleman Presidential Furnace

Posted: Thu Nov 15, 2007 7:37 am
by jford89
What would I be looking for? A transformer or something similar.
Thanks again

RE: Coleman Presidential Furnace

Posted: Thu Nov 15, 2007 3:21 pm
by hvac1000
Usually the transformer makes that jind of noise. It is common.