Hope you can help me i have a Nordyne electric furnace
model# E2EB-020HB sometimes when the heat kicks on it make a loud electric humming sound i can turn the furnace off and back on at the T-stat then it runs quite. And sometimes the furnace will kick on and run for a few seconds then it kicks off and on again by it's self i replaced the transformer thinking that was what is was any ideals it's getting cold outside thanks.
Nordyne electric furnace model# E2EB-020HB trouble
Hi,
Go to this page:
http://www.mobilehomerepair.com/NordyneElec.html
Contactor # 621958 @ $17.00 each . Your furnace has two of these in the circuits to the heating elements
Relay N.O. #621898 (Cooling) @ $7.44
Relay N.C. # 621899 (Heating) @ $8.25
These two relays are in the circuits to the blower motor for heating and cooling modes.
All of these play into the circuits you mentioned and any one or more could cause the hum or be a part of this.
It would take understanding the wiring diagram and testing the circuits in action to know what is happening.
Any or all can be ordered from above page by adding to cart and ordering through PayPal or by calling toll free to 1-877-263-7860 after 9AM CST and charging to Visa or Mastercard.
If outside the U.S., let us know for added info.
From what you stated, I would suspect one or both Contactors for noise and 621899 relay for on/off/on/off of blower motor.
With that said, without total testing, I would replace all 4 as each can/will fail at some time due to contacts pitting from arcing when opening and closing often with calls for heat and cool.
Thanks.
Take care and best wishes,
Robert
Go to this page:
http://www.mobilehomerepair.com/NordyneElec.html
Contactor # 621958 @ $17.00 each . Your furnace has two of these in the circuits to the heating elements
Relay N.O. #621898 (Cooling) @ $7.44
Relay N.C. # 621899 (Heating) @ $8.25
These two relays are in the circuits to the blower motor for heating and cooling modes.
All of these play into the circuits you mentioned and any one or more could cause the hum or be a part of this.
It would take understanding the wiring diagram and testing the circuits in action to know what is happening.
Any or all can be ordered from above page by adding to cart and ordering through PayPal or by calling toll free to 1-877-263-7860 after 9AM CST and charging to Visa or Mastercard.
If outside the U.S., let us know for added info.
From what you stated, I would suspect one or both Contactors for noise and 621899 relay for on/off/on/off of blower motor.
With that said, without total testing, I would replace all 4 as each can/will fail at some time due to contacts pitting from arcing when opening and closing often with calls for heat and cool.
Thanks.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne model m1mb 070a bw power issue
by Combustibleink » Mon Nov 16, 2020 10:21 am » in Nordyne Service & Repair - 0 Replies
- 115951 Views
-
Last post by Combustibleink
Mon Nov 16, 2020 10:21 am
-
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 65335 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-
-
-
Replace relay for Emergency. Heat in E2EB-15HB
by istvv4848 » Tue Oct 23, 2018 10:49 am » in Nordyne Service & Repair - 0 Replies
- 44206 Views
-
Last post by istvv4848
Tue Oct 23, 2018 10:49 am
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167296 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne M1B1 furnace issue - thermostat c wire not hooked up correctly. It's running off atteries instead
by Tallestt » Mon Apr 20, 2020 6:27 am » in Nordyne Service & Repair - 1 Replies
- 43235 Views
-
Last post by taurolyon
Tue Jun 23, 2020 4:02 pm
-