Page 2 of 3

Posted: Mon Oct 15, 2007 7:21 pm
by lindav
well there are 5 wires coming out of it, 3 black, 1 blue and 1 yellow. ????weird yes????

RE: evcon furnace with motor constantly running

Posted: Mon Oct 15, 2007 8:49 pm
by hvac1000
That is strange. Could be Robert will be along in a while. At this point I am kind of lost. Was there somekind of a part number on the old one? post all the numbers on the old one if you can.

RE: evcon furnace with motor constantly running

Posted: Mon Oct 15, 2007 9:30 pm
by Robert
Ok, is there a possibility it has just 4 spades and on one is something like this:

http://www.mobilehomerepair.com/media/img/G21-414.jpg


or this:


http://www.mobilehomerepair.com/media/img/G31-929.jpg


and it has two wires to it.


That would be 5 wires, but just 4 spades.




Thanks,
Robert

Posted: Mon Oct 15, 2007 9:31 pm
by lindav
ok so the numbers at the top are 84-50902-101b and at the bottom is 8665-309

Posted: Mon Oct 15, 2007 9:36 pm
by lindav
oh yes that is very possible, so now what do i do, as i only have one blue (should have 2) and 3 blacks (should have 2) and i have a yellow which i dont know what to do with.

RE: evcon furnace with motor constantly running

Posted: Mon Oct 15, 2007 9:39 pm
by Robert
Hi,


You should have 2 Blue and 2 Blacks = 4 wires.



Since you have a Yellow making it 5 wires, see if you had one of those terminals like above with 2 wires connected to it ?



Thanks,
Robert

Posted: Mon Oct 15, 2007 9:42 pm
by lindav
yes i believe it is like that, the two are very close together, looks like could be the same. two black wires are on that one, blue one is in the middle, another black one on the side and the yellow on the bottom

RE: evcon furnace with motor constantly running

Posted: Mon Oct 15, 2007 9:48 pm
by Robert
Is the relay next to the transformer inside the rectangular metal box at midway of furnace front ?



Just making sure we're on same page here.



If so, can you turn all power to furnace OFF, then remove those two blacks to see if they were on ONE spade by way of a terminal like I posted ?



Thanks,
Robert

Posted: Mon Oct 15, 2007 9:52 pm
by lindav
yes they are on one

RE: evcon furnace with motor constantly running

Posted: Mon Oct 15, 2007 9:54 pm
by Robert
Ok, so it only has 4 spades the same as the new one,,,,,,,,correct ?



Do you know where the wires go on new one or need help with that ?




Thanks,
Robert

Posted: Mon Oct 15, 2007 9:57 pm
by lindav
i would love you to help me with that, it just confuses me that i have one extra wire, i am assuming that the yellow goes elsewhere???

RE: evcon furnace with motor constantly running

Posted: Mon Oct 15, 2007 10:07 pm
by Robert
Ok, draw on a piece of paper the shape of the old relay.

Put a mark where each wire goes and the color.


At place of the two blacks, write 2 blacks.


Tape those two blacks together so as to know they are THE two blacks.



Then remove the wires and remove screws to remove the relay.



Lay it beside the drawing you made.


Look at the relay, it should have numbers beside each spade.



What are they and with what wire ?



Give me this and I'll see if same numbers match for both relays.



Thanks,
Robert

Posted: Mon Oct 15, 2007 10:38 pm
by lindav
ok i think i have this figured out, amazing hey? both blacks are linked together somehow and are on prong #2, yellow is on prong #3 the single black is on prong #4 and the blue is on prong #1. how does that sound?

RE: evcon furnace with motor constantly running

Posted: Mon Oct 15, 2007 10:49 pm
by Robert
Can you see at all where they go ?

Should be ok, but without testing, would like to be sure.


IF that is where they went on old relay, placing on same on new one should be fine though.


Thanks,
Robert

RE: evcon furnace with motor constantly running

Posted: Mon Oct 15, 2007 10:52 pm
by hvac1000
Thank you Robert I never thought that someone would mistake a two wire tie in for two separate wires. LOL At least now it is straitened out.