I am having problems with my blower fan running constantly. Yesterday I replaced the sequencer in my unit Part #3110-3571 with no effect. I am wondering if it may be the thermostat. Someone had said it may be the relay, but would the blower still work if the relay was bad? No matter what setting the thermostat is on, the blower constantly blows, this is why I believe it may be the thermostat. And if it is the thermostat, would a thermostat from Lowes or Home Depot work with my unit.
I am also having trouble with the water not running down the pvc pipe, I have tried bleach but no luck. I don't know if it's just too much water at one time because it will not turn off or what.
Coleman-Evcon EB10B
More that likely the relay is defective because it is stuck on.
It could also be a pinched wire or the thermostat.
You would be better off checking the 24 volt control circuit with a meter to see exactly which part is defective instead of just replacing parts.
It could also be a pinched wire or the thermostat.
You would be better off checking the 24 volt control circuit with a meter to see exactly which part is defective instead of just replacing parts.
God, grant me the serenity
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
to accept the things I cannot change;
the courage to change the things I can;
and the wisdom to know the difference.
Well the only thing is....I do not know anything about meters and testers and those sort of things.
How many wires connect to your t-stat ?
Turn power OFF, remove red wire connected to t-stat, turn power back ON.
Did the blower stop or keep running ?
If it stopped, most likely the t-stat.
If it keeps running, either the blower relay contacts are stuck or you have a short between two wires.
After t-stat test, if still running, go to blower relay.
Turn power OFF, remove one of the two coil wires from 1 or 3 .
Turn power back ON, did it stop ?
If so, you have a short, call a Tech.
If not and it is still running, most likely the blower relay is faulty.
It is Fan Relay # 3110-3301 @ $27.14 + $6.75 shipping.
It can be seen and ordered from here:
http://www.mobilehomerepair.com/ColemanElec.html
It is 3rd from bottom on right side column.
If needed, to order, add item to cart and order through PayPal
or call toll free to 1-877-263-7860 and charge to Visa or
Mastercard.
Thanks for inquiring and allowing us to assist you.
Take care and best wishes,
Robert
Turn power OFF, remove red wire connected to t-stat, turn power back ON.
Did the blower stop or keep running ?
If it stopped, most likely the t-stat.
If it keeps running, either the blower relay contacts are stuck or you have a short between two wires.
After t-stat test, if still running, go to blower relay.
Turn power OFF, remove one of the two coil wires from 1 or 3 .
Turn power back ON, did it stop ?
If so, you have a short, call a Tech.
If not and it is still running, most likely the blower relay is faulty.
It is Fan Relay # 3110-3301 @ $27.14 + $6.75 shipping.
It can be seen and ordered from here:
http://www.mobilehomerepair.com/ColemanElec.html
It is 3rd from bottom on right side column.
If needed, to order, add item to cart and order through PayPal
or call toll free to 1-877-263-7860 and charge to Visa or
Mastercard.
Thanks for inquiring and allowing us to assist you.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 0 Replies
- 105852 Views
-
Last post by cwwhite75
Sat Feb 29, 2020 8:46 am
-
-
Colman evcon presidental 7980B856 furnace will not stay on
by ezridersid » Sat Dec 21, 2019 8:52 pm » in Mobile Home Repair - 1 Replies
- 16422 Views
-
Last post by ezridersid
Sat Dec 21, 2019 9:04 pm
-
-
-
Transformer burning out in an Evcon DES 80
by BigDave67s » Wed Dec 29, 2021 10:01 pm » in Coleman Service & Repair - 0 Replies
- 107609 Views
-
Last post by BigDave67s
Wed Dec 29, 2021 10:01 pm
-
-
-
Evcon Heat Pump - Air Conditioner Model No. BRHS036B Making HUM Before Starting
by Dave_L » Tue Aug 29, 2023 1:26 am » in Coleman Service & Repair - 0 Replies
- 118735 Views
-
Last post by Dave_L
Tue Aug 29, 2023 1:26 am
-
-
- 2 Replies
- 57129 Views
-
Last post by jazsimpson
Sat Jul 08, 2017 8:16 am