Hi Ricky,
Let me get caught up on some of these forum questions and read over what you wrote in last reply and then I'll give you some tests to do to get to bottom of your problem.
Thanks,
Robert
Intertherm FEH 015HA-03 Blower will not start
Hi Ricky,
What happened when you changed setting to HG and t-stat set to heat-auto-85* ?
Try it with jumper removed .
Thanks,
Robert
What happened when you changed setting to HG and t-stat set to heat-auto-85* ?
Try it with jumper removed .
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Posts: 10
- Joined: Wed Dec 30, 2009 11:28 pm
Robert
As you suggested, I tried the t-stat in HG ans it did not correct the problem. With the jumper removed, the blower will come on when the t-stat is set to heat, and fan set to on.
Suggestions?
I received the relay and will install it.
Thanks
Ricky
As you suggested, I tried the t-stat in HG ans it did not correct the problem. With the jumper removed, the blower will come on when the t-stat is set to heat, and fan set to on.
Suggestions?
I received the relay and will install it.
Thanks
Ricky
Hi Ricky,
IF replacing the relay doesn't resolve it, then go to BOTH transformers and test each.
Primary-Line = 240vac
Secondary-Load = 24vac
Thanks,
Robert
IF replacing the relay doesn't resolve it, then go to BOTH transformers and test each.
Primary-Line = 240vac
Secondary-Load = 24vac
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Posts: 10
- Joined: Wed Dec 30, 2009 11:28 pm
Robert
The xfmr at the furnace has 24 vac when measured between the red wire going to the t-stat and the black wire going to the sequencer. There is 240 on the primary side.
I haven't checked the xfmr on the AC yet. But I will and will let you know.
With the t-stat set to HG, auto and set to demand heat with jumper removed the blower does not come on.
Regarding the relay, the one installed is an after market honeywell with 10 terminals. The one I ordered has only the six required terminals. The wiring schematic/diagram does not show the relay, but says install relay IAW diagram on relay. However, the OEM relay does not have a diagram. If possible, please identify where terminals 1 thru 6 on the relay should be connected.
Thanks
Ricky
The xfmr at the furnace has 24 vac when measured between the red wire going to the t-stat and the black wire going to the sequencer. There is 240 on the primary side.
I haven't checked the xfmr on the AC yet. But I will and will let you know.
With the t-stat set to HG, auto and set to demand heat with jumper removed the blower does not come on.
Regarding the relay, the one installed is an after market honeywell with 10 terminals. The one I ordered has only the six required terminals. The wiring schematic/diagram does not show the relay, but says install relay IAW diagram on relay. However, the OEM relay does not have a diagram. If possible, please identify where terminals 1 thru 6 on the relay should be connected.
Thanks
Ricky
Hi Ricky,
1 = 24vac common side of transformer
3 = G on t-stat
5 = sequencer M 2
6 = Blower motor heat speed (low)
2 = furnace breaker
4 = Blower motor cool speed (high)
Thanks,
Robert
1 = 24vac common side of transformer
3 = G on t-stat
5 = sequencer M 2
6 = Blower motor heat speed (low)
2 = furnace breaker
4 = Blower motor cool speed (high)
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 167292 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
heater blower intertherm feh-015ha-03
by newguy47 » Wed Oct 24, 2018 8:04 am » in Nordyne Service & Repair - 0 Replies
- 84663 Views
-
Last post by newguy47
Wed Oct 24, 2018 8:04 am
-
-
-
intertherm feh-015ha-04 Noisy Blower
by kjaxes99 » Sat Oct 24, 2020 4:45 am » in Nordyne Service & Repair - 0 Replies
- 141301 Views
-
Last post by kjaxes99
Sat Oct 24, 2020 4:45 am
-
-
- 0 Replies
- 78333 Views
-
Last post by newguy47
Thu Aug 16, 2018 8:21 pm
-
-
Intertherm FEH-017HAC won't shut off
by Jetherid » Mon Dec 07, 2020 6:22 pm » in Nordyne Service & Repair - 0 Replies
- 175194 Views
-
Last post by Jetherid
Mon Dec 07, 2020 6:22 pm
-