I have finally gotten my Nordyne E1EHA-015 re-wired, it helped when I found the wiring diagram for the 4 to 7 Control Box.
Now since I replaced the control box with relays here is the problem that I have run into, when the heat signal (24V) is stopped the fan turns off but the elements are still on unti the Sequencer times out.
What would recomend as a work around to keep the fan running til after the elements de-engerize??
Heating after fan stops running
I solved the problem by adding a Off-Delay Timer and doing away with the heating relay that I setup to replace the 4-7 Control Board.
The timer is adjustable for the amount of time to allow the fan to run, I set it at alittle over 2 minutes. This gives the elements a chance to cool down before the fan stops running.
The timer is adjustable for the amount of time to allow the fan to run, I set it at alittle over 2 minutes. This gives the elements a chance to cool down before the fan stops running.
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Unit Starts then Stops - Ignition Failure
by Arkady78 » Wed Dec 02, 2020 9:58 am » in Coleman Service & Repair - 0 Replies
- 100668 Views
-
Last post by Arkady78
Wed Dec 02, 2020 9:58 am
-
-
-
Heat strip on while AC is running HELP Please!
by HelpNeeded » Wed Sep 19, 2018 6:47 pm » in Coleman Service & Repair - 0 Replies
- 33302 Views
-
Last post by HelpNeeded
Wed Sep 19, 2018 6:47 pm
-
-
-
Nordyne M1B1 furnace issue - thermostat c wire not hooked up correctly. It's running off atteries instead
by Tallestt » Mon Apr 20, 2020 6:27 am » in Nordyne Service & Repair - 1 Replies
- 40143 Views
-
Last post by taurolyon
Tue Jun 23, 2020 4:02 pm
-
-
- 0 Replies
- 27965 Views
-
Last post by Carl Wofford
Sat Jan 20, 2018 6:55 pm
-
-
Coleman 6806a furnace doesn't stop heating even with tstat disconnected. Any ideas?
by Neighbor Bill » Mon Dec 31, 2018 1:01 pm » in Coleman Service & Repair - 1 Replies
- 38758 Views
-
Last post by Neighbor Bill
Mon Dec 31, 2018 1:06 pm
-