Nordyne Intertherm E2EB-020HB
I have a heater/a/c unit in my mobile home. Air seems to work fine. Fan seems to work fine. I turn to heat and nothing. I tried turning the thermostat up still nothing. have checked all the breakers. Everything seems fine. When I turn to heat I hear no clicks no fan nothing. It has worked fine for the last couple of months. Just noticed the house getting chilly so it couldn't have been off to long as its about 10 degrees outside. Not sure where to go from here.
Hi,
Your furnace has two contactors and two relays that together control the elements and the blower motor .
The circuits can run through them even though that one may not actually control the circuit or component.
Without thorough electrical testing, hard to say which one may be at fault or if it's something else entirely.
With what you stated however,one or more of those would be most common to be at fault.
Contactor # 621958 (2 of them)
Relay N.O. # 621898
Relay N.C. # 621899
Go here and page down to see and order contactors:
http://www.aberdeenhomerepair.com/store ... p-24V-coil
Then type in relay p/n's one at a time to see and order those.
Thanks,
Robert
Your furnace has two contactors and two relays that together control the elements and the blower motor .
The circuits can run through them even though that one may not actually control the circuit or component.
Without thorough electrical testing, hard to say which one may be at fault or if it's something else entirely.
With what you stated however,one or more of those would be most common to be at fault.
Contactor # 621958 (2 of them)
Relay N.O. # 621898
Relay N.C. # 621899
Go here and page down to see and order contactors:
http://www.aberdeenhomerepair.com/store ... p-24V-coil
Then type in relay p/n's one at a time to see and order those.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 164122 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 64276 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-
-
-
Replace relay for Emergency. Heat in E2EB-15HB
by istvv4848 » Tue Oct 23, 2018 10:49 am » in Nordyne Service & Repair - 0 Replies
- 43328 Views
-
Last post by istvv4848
Tue Oct 23, 2018 10:49 am
-
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 53505 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 73031 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-