The main gas valve ignites fine ! but only stays on for 5 or 6 seconds then dies!!! The flame sensor does detect a flame for those 5 or 6 seconds (yellow led glows steady). I've replaced the glow plug/sensor. I've replaced the entire gas valve. Still no luck!!
By the way the furnace is 2 years old but I have personally never seen it work. Jonathan 727-5424294
Nordyne M1MB 090A Burner won't remain lit
Hi Jonathan,
If it never has worked, did you ever call out a Tech while still under warranty ?
Place meter leads on the gas valve terminals and see if the gas valve remains energized at time it stops or does it lose the 24-28VAC.
Thanks,
Robert
If it never has worked, did you ever call out a Tech while still under warranty ?
Place meter leads on the gas valve terminals and see if the gas valve remains energized at time it stops or does it lose the 24-28VAC.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 2 Replies
- 17696 Views
-
Last post by TorstenW
Tue Mar 06, 2018 1:04 am
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 43302 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-
-
-
Nordyne model m1mb 070a bw power issue
by Combustibleink » Mon Nov 16, 2020 10:21 am » in Nordyne Service & Repair - 0 Replies
- 107599 Views
-
Last post by Combustibleink
Mon Nov 16, 2020 10:21 am
-
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 48868 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 67883 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-