Central Electric Furnace is only blowing cool air.

Post all other heating and cooling questions here.

Moderators: Greg, Mark

Locked
jbkeeley84

I have a Central Electric Furnace. The model number - EB17B and the serial number - W0H5698597. The Problem is that is only is blowing cool air. It is a fairly new furnace (less than 5 years) and I cleaned off all the dust I could. I also found stamped inside "Coleman 7681-607" If anyone has any tips or has run into a similar problem and could help that would be great. Thanks - Jonny
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi Jonny,

Are you getting 240vac across each element coil end terminals ?



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
jbkeeley84

Hello,
Thanks for you reply to my question. It turns out that it was a bad sequencer. Thanks again for this great site it has helped a lot. - Jonny
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

You're very welcome, happy to help.



Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?