Intertherm mod feh015hr-03

Questions about repairs and parts for other brands of furnaces and air conditioners. Please note that our speciality is Coleman and Nordyne products, so our knowledge of other brands may be limited.

Moderators: Greg, Mark

Locked
icoon
Posts: 2
Joined: Mon Oct 08, 2012 5:48 pm

electric furnace and air cond.Air has worked good all summer, turned on heat and it came on and worked ok for 1 day. Got up this am and turned thremo up for heat nothing happened at all ,tried air no go tried fan only no go will not do anything checked main breakers all are on.what do i check next??? thanks in advance for any answers.
DaleM
Posts: 385
Joined: Wed Apr 07, 2010 10:07 am

Check to see if the transformer is putting out 24 volts.
icoon
Posts: 2
Joined: Mon Oct 08, 2012 5:48 pm

Thanks for the reply,upon further inspection i found out that the fuse panel was the problem .One of the 60 amp fuses had blown due to the top of the fuse connector overheating and burning up the bakeolite panel where the connector was attached. I JB welded it back in place for the time being.I need a new panal. Mine has the 60 amp fuses on the inside and the 30 amp on the outside.Any ideas on a replacement??