FEH-0208A-03 or FEH-020HA-03

Posted: Fri Nov 05, 2010 4:24 pm
by Oletrapper
I have an old Intertherm in our deer camp. Numbers above. Only works when fan switch is turned to fan-on. The rocker on the switch was broken and I replaced the switch thinking that was why it was not working on auto.

When on auto, therm calling for heat, coil heats up and there is a click and coil shuts down. I am suspecting the sequencer but not sure. Any help would be appreciated. Also need part # if you think that is the problem.

Thanks, OT

Re: FEH-0208A-03 or FEH-020HA-03

Posted: Sat Nov 06, 2010 2:30 am
by Robert
Hi OT,

Sequencer # 901076 can be seen and ordered from here by paging down to it:

http://www.aberdeenhomerepair.com/store ... -sequencer


That sounds like it would be most common for what you stated.



Thanks,
Robert

Re: FEH-0208A-03 or FEH-020HA-03

Posted: Sat Nov 06, 2010 5:55 am
by Oletrapper
Thanks Robert, Just ordered. As far as the numbers above. Tag is worn and could not tell if it is HA or 8A. Noticed on several posts it was listed both ways. Thanks again. OT

Re: FEH-0208A-03 or FEH-020HA-03

Posted: Sun Nov 07, 2010 1:19 am
by Robert
Hi OT,

You're very welcome, happy to help. Thanks for ordering with us.

It is FEH-020HA


Thanks,