I have a problem with this furnace.
It will run fine for a while, then out of the blue its starts to get cool in the house.
When i check the furnace the power is off. I turn the power switch off and back on then it will run fine and then out off the blue it will do it again. Any suggestions?
User avatar
Greg
Moderator
Posts: 5696
Joined: Wed Feb 28, 2007 8:01 pm
Location: Weedsport, NY

I'm going to move this to the heating section of the site.
"If I can't fix it, I can screw it up so bad no one else can either."
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

When it does it, test transformer and input power wires to furnace for power.

Need 24VAC low voltage from transformer to t-stat to furnace.

Also need 120VAC line voltage to furnace through the breaker(s) and transformer.


Thanks,
Robert