Induced Draft Blower runs all the time.

Questions about repairs and parts for other brands of furnaces and air conditioners. Please note that our speciality is Coleman and Nordyne products, so our knowledge of other brands may be limited.

Moderators: Greg, Mark

Locked
mark_leon
Posts: 1
Joined: Wed Sep 02, 2009 6:06 pm

Hello,

I have a Gibson KG6RC-040C-08A.

The AC and heat work just fine, switching on and off according to the thermostat setting, but the induced draft blower runs all the time.

Thermostat to off, batteries out, batteries in, heat on, heat off, ac on, ac off, doesn't matter. Only way to stop it from running is to remove power from the unit or at the breaker box.

The control panel is NORDYNE PT# 624631-B 1012 955a

The yellow and red LED's are on constant...no flashes.

I reseated all the connections to the control panel hoping that would help and tested again, but it's still the same.

Any ideas?

Thanks!

-Mark
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi Mark,


Probably a bad control board. Would need to test to know for sure.


If you need help with testing it, go here for info :

http://www.mobilehomerepair.com/Order4b.html


We have the board if needed also.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?