I have an " InterTherm" electric furnace (1996 Mobile Home) that when the thermostat calls for heat the elements heat up and kick off after several seconds because the blower dose'nt kick on. This has been an intermittent problem for a few days until today.
I can make the blower run from the T-stat or by moving the switch on the furnace to auto so I don't believe the problem is in the blower or the t-stat.
Any ideas??
Thanks........Rich
Elements heat up by Blower does'nt come on
Hi Rich,
For your furnace, you have 3 element coils.
The sequencer has 3 sets of contacts, one for each element.
ONE of those three also controls the blower.
So, if that set fails, the other two will still energize thier elements, but the one for the element/blower will not.
Sequencer # 01-0842 can be seen and ordered through Paypal
from this page on left side :
http://www.mobilehomerepair.com/NordyneElec.html
Thanks,
Robert
For your furnace, you have 3 element coils.
The sequencer has 3 sets of contacts, one for each element.
ONE of those three also controls the blower.
So, if that set fails, the other two will still energize thier elements, but the one for the element/blower will not.
Sequencer # 01-0842 can be seen and ordered through Paypal
from this page on left side :
http://www.mobilehomerepair.com/NordyneElec.html
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Eb15a elec furnace will only come on if jumpered at themostat
by redcat31 » Wed Jan 31, 2018 6:18 pm » in Service & Repair of Other Brands - 0 Replies
- 19848 Views
-
Last post by redcat31
Sat Feb 03, 2018 1:20 am
-
-
- 2 Replies
- 17377 Views
-
Last post by TorstenW
Tue Mar 06, 2018 1:04 am
-
- 0 Replies
- 21759 Views
-
Last post by nestsman
Sat Aug 19, 2017 1:47 pm
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 48194 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-
-
-
Acceptable HEAT RISE number for this 20-yr. old furnace.
by justplumducky » Tue Aug 29, 2017 5:33 pm » in Nordyne Service & Repair - 0 Replies
- 38635 Views
-
Last post by justplumducky
Tue Aug 29, 2017 5:33 pm
-