i have a intertherm furnace model feh-017h. the problem here is it keeps blowing fuses or are burnt.the furnace keeps running and won't shut down using the thermostat. a repair guy came over and said it is the sequencers .this model has two on a metal plate.
i don't have manual and i don't know which ones to buy. i called a furnace parts and said , need part number off of sequencers. this a 1981 furnance and my stepson doesn't want to buy a new furnace.
another forum says its the heat kit that causes to blow fuses.any help on this and does anyone have a part number for the sequencers or do you think its the heat kit.
thanks.
intertherm furnance not shutting down
Hi,
Could be just the sequencer or could be both. Would have to test voltages and amp draw to know for sure.
Sequencer most likely keeping it running. That fault or a bad disconnect assembly could be causing fuses to blow.
Sequencer # 901075
Disconnect Assembly # 621029
Either or both can be seen and ordered through PayPal from
this page here :
http://www.mobilehomerepair.com/NordyneElec.html
A reputable hvac tech could diagnose and tell you for sure.
Thanks,
Robert
Could be just the sequencer or could be both. Would have to test voltages and amp draw to know for sure.
Sequencer most likely keeping it running. That fault or a bad disconnect assembly could be causing fuses to blow.
Sequencer # 901075
Disconnect Assembly # 621029
Either or both can be seen and ordered through PayPal from
this page here :
http://www.mobilehomerepair.com/NordyneElec.html
A reputable hvac tech could diagnose and tell you for sure.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi,
Please start a new thread with your question to keep confusion down,
Then come back here and delete the post here.
Thanks,
Robert
Please start a new thread with your question to keep confusion down,
Then come back here and delete the post here.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Furnance continues to click, Fan always on
by rcrown1872 » Tue Oct 01, 2019 11:55 am » in Nordyne Service & Repair - 0 Replies
- 19969 Views
-
Last post by rcrown1872
Tue Oct 01, 2019 11:55 am
-
-
- 0 Replies
- 22360 Views
-
Last post by Tonystark
Fri Dec 07, 2018 12:30 pm
-
-
3500A816 Randomly wont start or shut down
by Smithcraft » Fri Jan 13, 2023 4:04 pm » in Coleman Service & Repair - 0 Replies
- 80305 Views
-
Last post by Smithcraft
Fri Jan 13, 2023 4:04 pm
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 60452 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 99313 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-