Intertherm Model MGH-065 random turn-on

Posted: Mon May 13, 2013 10:30 pm
by greyharte
so here's the issue, I have an older Intertherm Model MGH-065A gas heater (furnace?), regardless of whether the ambient temperature dictates the need (70+), and the thermostat turned down to 50, the heater comes on, the only way to resolve this is to turn off the heater with the switch inside the enclosure. I would really like to not have to turn off the heater outright since we still get random cold nights. the thermostat in use is a Honeywell CT30A1005 I believe.

any suggestions on what/how to resolve this??

btw the thermostat is an non-mercury type unit, though I did make sure that is was level, I have also thoroughly cleaned both thermostat (wasn't really dirty at all) and the heater control box (removed cover) as well as the heater cabinet.

Re: Intertherm Model MGH-065 random turn-on

Posted: Tue May 14, 2013 9:10 pm
by DaleM
When this happens is the burner actually firing?

Re: Intertherm Model MGH-065 random turn-on

Posted: Tue May 21, 2013 4:40 pm
by greyharte
yes, heater actually turns fully on

Re: Intertherm Model MGH-065 random turn-on

Posted: Wed May 22, 2013 3:26 pm
by JeffInFL
Some furnaces have a control board which could go bad and cause weird things to happen, like the blower kicking on & off

Re: Intertherm Model MGH-065 random turn-on

Posted: Sun May 26, 2013 2:58 pm
by jpingram5
If you can get your hands another a used working thermostat or a new cheap one, I would suggest trying that first just to eliminate the Thermostat. Do you ever here the Thermostat click when the heat randomly turns on? That's where I would start I've come across a lot strange problems with thermostats being the culprit.

Re: Intertherm Model MGH-065 random turn-on

Posted: Sun May 26, 2013 3:21 pm
by DaleM
Pick up a cheap heat only tstat and wire that into just the furnace. Eliminate the original tstat and all it's wiring. See what happens. Sounds like either a varmint chewed through a wire and when they touch the circuit completes turning on the heat or a screw was run through the original wire and now years later the problem shows itself.