Intertherm Model MGH-065 random turn-on

Questions about repairs and parts for other brands of furnaces and air conditioners. Please note that our speciality is Coleman and Nordyne products, so our knowledge of other brands may be limited.

Moderators: Greg, Mark

Locked
greyharte
Posts: 2
Joined: Mon May 13, 2013 6:16 pm

so here's the issue, I have an older Intertherm Model MGH-065A gas heater (furnace?), regardless of whether the ambient temperature dictates the need (70+), and the thermostat turned down to 50, the heater comes on, the only way to resolve this is to turn off the heater with the switch inside the enclosure. I would really like to not have to turn off the heater outright since we still get random cold nights. the thermostat in use is a Honeywell CT30A1005 I believe.

any suggestions on what/how to resolve this??

btw the thermostat is an non-mercury type unit, though I did make sure that is was level, I have also thoroughly cleaned both thermostat (wasn't really dirty at all) and the heater control box (removed cover) as well as the heater cabinet.
DaleM
Posts: 385
Joined: Wed Apr 07, 2010 10:07 am

When this happens is the burner actually firing?
greyharte
Posts: 2
Joined: Mon May 13, 2013 6:16 pm

yes, heater actually turns fully on
User avatar
JeffInFL
Posts: 171
Joined: Wed Apr 24, 2013 6:52 am

Some furnaces have a control board which could go bad and cause weird things to happen, like the blower kicking on & off
jpingram5
Posts: 205
Joined: Sun Dec 05, 2010 5:34 pm
Location: Orefield, PA
Contact:

If you can get your hands another a used working thermostat or a new cheap one, I would suggest trying that first just to eliminate the Thermostat. Do you ever here the Thermostat click when the heat randomly turns on? That's where I would start I've come across a lot strange problems with thermostats being the culprit.
2009 Skyline Sunwood Premier 14 x 80
DaleM
Posts: 385
Joined: Wed Apr 07, 2010 10:07 am

Pick up a cheap heat only tstat and wire that into just the furnace. Eliminate the original tstat and all it's wiring. See what happens. Sounds like either a varmint chewed through a wire and when they touch the circuit completes turning on the heat or a screw was run through the original wire and now years later the problem shows itself.