e2eb-012ha heat and ac both at the same time
Posted: Wed Oct 19, 2011 8:48 pm
1st of hi
ok here goes weve got a e2eb-012ha unit and the ac has been fine this summer now its getting cold we turned the heater on and it didnt work ,i looked in there and the sequencer was just about falling apart i replaced the sequencer and now when you trip the main breaker back on the blower motor will come on but only runs for like 15-20 seconds but the fan is also running on the ac unit outside and is blowing cold air ,after the blower fan stops around 15 seconds later the heater elements wil start to cycle but the blower isnt running although the outside ac is running ,the thermostat on the wall is set to heat and set a couple of degrees hotter than its reading ,if you turn the ac back on it works fine ,everything looks to be ok in there nothings burnt etc if anyone could help and point me in the right direction it would be great
ok here goes weve got a e2eb-012ha unit and the ac has been fine this summer now its getting cold we turned the heater on and it didnt work ,i looked in there and the sequencer was just about falling apart i replaced the sequencer and now when you trip the main breaker back on the blower motor will come on but only runs for like 15-20 seconds but the fan is also running on the ac unit outside and is blowing cold air ,after the blower fan stops around 15 seconds later the heater elements wil start to cycle but the blower isnt running although the outside ac is running ,the thermostat on the wall is set to heat and set a couple of degrees hotter than its reading ,if you turn the ac back on it works fine ,everything looks to be ok in there nothings burnt etc if anyone could help and point me in the right direction it would be great