Blower Questions E1EH1-015A

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
jelrod55
Posts: 8
Joined: Mon Oct 03, 2011 2:00 pm

:shock: HVAC repairman replaced blower on unit ($375.00), but could not get it to work, so 2nd service man called in.
2nd Repairman, said problems must be in control board, so he installed a fan contactor and set up the motor on high speed. Which is okay for cooling, but motor is supposed to run on low speed for heat (I think).

How would I change this motor over to low speed or is it okay on high?

Please no more repairmen as I now have over $1100.00, with the last 2.

The motor diagram shows Black and White wires for High Speed
Blue and White wiresfor Med speed
Red and White wires for Low speed

Thank you in advance.
User avatar
Mark
Site Admin
Posts: 742
Joined: Sat Feb 17, 2007 4:23 pm
Location: Aberdeen, SD
Contact:

Remove the black wire and put the red wire in its place.

Mark
You can't fail if you don't try!