Intertherm FEH015HA-04 Wont shut down.

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
justinieon
Posts: 1
Joined: Tue Feb 08, 2011 11:31 pm

Our Heating unti has been running constantly for a while. checked temps at t-stat and around house and all are above what system is set to. We changed the t-stat thinking it was bad. i was told the unit worked normally for the first part of the day and then proceeded to run constantly. Only way to stop system is to use breaker to shut it off. I am thinking it could be the sequencer but i was wondering if anyone had any other ideas.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,


Most likely a stuck sequencer.


Sequencer # 901075 can be seen and ordered from here by paging down :

http://www.aberdeenhomerepair.com/store ... er-3-stage




Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?