dont know if this is the wright place but here goes got a nordyne m1mb 090 aaw light flashes that the pressure switch is open so have changed it new induser motor checked hoses draft is 1.5 checked exhaust as well as intake all clear any one got any thoughts thanks
need to add more to first post when i check voltage to pressure switch running reads 24 v on both sides when t stat temp is reached and every thing shuts down one side reads 4.2 should it read 4.2 then seams to me when shut down both sides should read 0 if so any thoughts thanks
Remove one wire and ohm across it to see if it is open or closed.
Sometimes they will read a small voltage through a back feed.
Thanks,
Robert
Sometimes they will read a small voltage through a back feed.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
did what you asked reads 0 one thing dont understand can mess with it and will run fine for a couple hrs then flashes code switch is open and i jumped around it and worked fine just jumped it for a minute could it be in the board with a relay could one be getting hot after a time
IF it is an intermittent problem, could be several things. Will need an hvac tech to do some specific tests to know what it is for sure.
Thanks,
Robert
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 41797 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-
-
-
Nordyne model m1mb 070a bw power issue
by Combustibleink » Mon Nov 16, 2020 10:21 am » in Nordyne Service & Repair - 0 Replies
- 104942 Views
-
Last post by Combustibleink
Mon Nov 16, 2020 10:21 am
-
-
-
Help with Nordyne electronic board
by swade1991 » Thu Aug 02, 2018 12:13 pm » in Nordyne Service & Repair - 0 Replies
- 27825 Views
-
Last post by swade1991
Thu Aug 02, 2018 12:13 pm
-
-
- 2 Replies
- 20684 Views
-
Last post by Maxwell.lipphardt
Mon Feb 04, 2019 6:35 am
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 150925 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-