Hello all,
I havea Nordyne E2EB-017HA unit in my Mfg Home. On AC everything works just fine. When the furnace heater is engaged, it randomly trips the bottom breaker on the unit itself.
It may go for several days without tripping this breaker and then it might trip this breaker within minutes. I can see the elements glowing and the unit. When this happens, the unit gets extremely hot to the touch and I am afraid to leave it on at all when on one is at the house.
Does anyone have any ideas as to the possible causes of this problem?
The blower I assume is working fine since it blows with the AC without issue.
Any ideas would be appreciated!
Nordyne Mod# E2EB-017HA - Furnace trips breaker periodically
Check inside for loose or burnt wires.
Remove blower assembly and look down on elements and see if any has broken or fallen and touching frame or each other.
May be a shorted circuit.
Thanks,
Robert
Remove blower assembly and look down on elements and see if any has broken or fallen and touching frame or each other.
May be a shorted circuit.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 138588 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne Mod. E1EH-015HA split unit/eliminate cooling?
by carolina jim » Thu Oct 24, 2019 8:33 am » in Nordyne Service & Repair - 0 Replies
- 29547 Views
-
Last post by carolina jim
Thu Oct 24, 2019 8:33 am
-
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 53639 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-
-
-
Replace relay for Emergency. Heat in E2EB-15HB
by istvv4848 » Tue Oct 23, 2018 10:49 am » in Nordyne Service & Repair - 0 Replies
- 34063 Views
-
Last post by istvv4848
Tue Oct 23, 2018 10:49 am
-
-
-
Nordyne M1B1 furnace issue - thermostat c wire not hooked up correctly. It's running off atteries instead
by Tallestt » Mon Apr 20, 2020 6:27 am » in Nordyne Service & Repair - 1 Replies
- 30639 Views
-
Last post by taurolyon
Tue Jun 23, 2020 4:02 pm
-