Blower will not kick on in auto
I have an E2EB-017HA that will not turn on in auto. I have replaced the sequencer thinking that was the problem but its still not kicking on. The blower will work in the on position but not in auto and it will heat up. It has worked correctly a few cycles when i first replaced the sequencer but then it would not start back up. Is it posssibly a fan relay?
Set t-stat to call for heat, wait 45 secs and then test and see if you have 240vac going to the heat speed wire and the common wire from breaker.
Usually red and orange or red and white from motor.
Is motor getting hot trying to start ?
Thanks,
Robert
Usually red and orange or red and white from motor.
Is motor getting hot trying to start ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 99113 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 141643 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 60330 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
-
Heat strips are on, but not the fan.
by Forestbrook » Sat Dec 08, 2018 6:09 pm » in Coleman Service & Repair - 0 Replies
- 33816 Views
-
Last post by Forestbrook
Sat Dec 08, 2018 6:09 pm
-
-
- 2 Replies
- 17783 Views
-
Last post by plumducky
Tue Dec 10, 2019 3:59 pm