fan runs continuous and heater elements warm with unit off

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
dbabuddy

i have a nordyne E2EB-015HA FURNACE WITH A/C. A- COIL FILLED UP WITH WATER AND DRIPPED ON DOWN TO FAN RELAY AND SEQUENCERS. WHEN UNIT IS OFF LOW SPEED FAN IS STILL ON AND I FEEL LOW HEAT AT THE ELEMENTS. WOULD LIKE TO REPLACE FAN RELAY AND IT LOOKS LIKE 2 SEQUENCERS , A DOUBLE POLE AND SINGLE POLE. ( THEY HAVE RUST ON THEM) WILL REPLACING ALL 3 SOLVE THE PROBLEM? WHAT ARE THE PART # . THANKS IN ADVANCE FOR ANY HELP
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

Sequencer # 621679 @ $35

Blower Relay # 621867 @ $13.53

Shipping = $12


First, you would need to correct water problem. Then, replacing those may or may not solve it.

Depends on whether any other parts were wet and damaged and/or shorts caused by the water.


Those are high possibilities.


You can see and order them from this page:

http://www.mobilehomerepair.com/NordyneElec.html


If interested, please add to cart and order through Paypal or call

toll free to 1-877-263-7860 and charge to Visa or Mastercard.


Thanks.


Take care and best wishes,
Robert