Blower runs continuously

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
early4nada

I have an Intertherm/Nordyne G5RA096C-16. Duing the night, we had a lightning strike that caused us to lose power. When the power company got the power back on, the furnace blower runs continuously regardless of the the thermostat setting (on/off/fan, etc...).

I checked the 120VAC, the 24VAC and ICM fuse and all looks good. The status led on the ICM (p/n 624557-0) is off, as in no power, even though there is power to the board.

Is it new control board time or is there something else I should check?

Thanks in advance for your help.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,


Turn t-stat to OFF and if blower keeps running, check to see if it is getting 24V to the board and 120V from control board .

IF there is not 24V to board from t-stat, but there is 120V from board going to motor, the board id faulty.


This may or may not be the whole problem either way, but is most likely.

I can give a price quote for the board if needed.


Thanks,
Robert