I came home and my thermostat was flashing no ac power and found I had a blown transformer. I have a 220 air handler with strip heat. I have tested the heat pump by pushing in the contactor test button it comes on. I replaced the transformer and the t stat still said no AC power after a long time I hit the reset button on the t stat and reprogrammed it. When the heat pump tries to come on it shut down everything and goes back to flashing no AC power!!! I was luck it did not take out the transformer again. The heat pump has a new start capictor and the cont actor has little pitting.
Am I looking at a bad board?
The airhandler seems to work fine
Intertherm Heat pump issue? need help!! model T3Q
Have you just installed the programable t-stat or has it been installed for awhile and everything has been working fine in the heat/cool and emergency heat mode? The reason I ask is that it sounds like you have a short somewhere in your 24v side of the system. If you just installed the stat you have to make sure that your C (common) wire that attaches to your t-stat,Air handler,and then goes to the outside unit does not mistakenly get connected to the other side of the 24v circuit. Look at your wiring (not just the color) and make sure that the wire on C terminal of your t-stat is the same wire on the C terminal of your air handler and goes to the C terminal on the outside unit and you have only this wire on your C terminals.. The wire I am referring to is the field installed low voltage wire. If the wiring looks ok check where it enters the airhandler and outside unit and see if some insulation has been worn away that causes the other wires not the C (common) wire to touch metal.
If your wiring looks ok and your air-handler runs fine in the fan only and emergency heat mode and you have never had to reset a breaker then heres where it gets tricky. You would have to have a meter a set of jumpers,and a lot of knowledge on the wiring diagram to pinpoint the problem. The possibilities are a bad contactor coil, defrost board, reversing valve solenoid(if 24V) or any other device in the LV-24V circuit. Some of these devices have both high and low voltage going to them so where you put your meter probes and hands can be dangerous. I would call out a tech because some of the items you can just disconnect the wires and test but a tech would install a fuse link in the system while he was testing to keep from shorting out another transformer. Also it can get quite expensive by parts changing without a clear indication that the part is bad. This is where the services of a licensed tech would save you money.
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Evcon Heat Pump - Air Conditioner Model No. BRHS036B Making HUM Before Starting
by Dave_L » Tue Aug 29, 2023 1:26 am » in Coleman Service & Repair - 0 Replies
- 126137 Views
-
Last post by Dave_L
Tue Aug 29, 2023 1:26 am
-
-
-
have intertherm heat pump with a 913421 control box tying to a miller 841 thermo stat ,
by hillcat01 » Mon Oct 21, 2019 7:28 pm » in Nordyne Service & Repair - 0 Replies
- 86603 Views
-
Last post by hillcat01
Mon Oct 21, 2019 7:28 pm
-
-
-
1989 Champion, entrance door issue, need advice
by hotrod53 » Mon Dec 30, 2019 5:33 pm » in Mobile Home Repair - 3 Replies
- 47206 Views
-
Last post by Greg
Tue Dec 31, 2019 7:27 pm
-
-
-
Nordyne model m1mb 070a bw power issue
by Combustibleink » Mon Nov 16, 2020 10:21 am » in Nordyne Service & Repair - 0 Replies
- 115798 Views
-
Last post by Combustibleink
Mon Nov 16, 2020 10:21 am
-
-
- 0 Replies
- 41794 Views
-
Last post by David DeBord
Sun Oct 22, 2017 7:13 am