Coleman DGAT075BDD problem

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
63Dream
Posts: 5
Joined: Mon Jan 21, 2013 9:24 am

I have a Coleman DGAT075BDD furnace that blowed the 3 amp fuse a few weeks ago so I replaced it and has worked fine until last night. I woke up cold and found the fuse blown again so I replaced it but the fan came on and would not go off and it was flashing a code 4. I started checking everything I thought it could be and foung that the upper limit switch has a reset and was triped. I reset it and repowered the unit and it has worked all day. My question is what caused this, is the board going bad or maybe the limit switch. Any help would be greatly appreciated.

Terry
User avatar
Greg
Moderator
Posts: 5696
Joined: Wed Feb 28, 2007 8:01 pm
Location: Weedsport, NY

Lets move this to the heating section.

Greg
"If I can't fix it, I can screw it up so bad no one else can either."
DaleM
Posts: 385
Joined: Wed Apr 07, 2010 10:07 am

Is there an air conditioner connected to this furnace? Is there a Blend Air system connected to this furnace?
63Dream
Posts: 5
Joined: Mon Jan 21, 2013 9:24 am

Yes it has the blend air system and it does have A/C. I checked to be sure the blend air was working after I got the heat working again and it was working.
DaleM
Posts: 385
Joined: Wed Apr 07, 2010 10:07 am

Disconnect all the Blend Air wiring on that unit. There has been a few instances where the Blend Air control board confuses the furnace's control board, sometimes it even causes it to fry out. Fortunately this time it was only the fuse. I am a Coleman warranty rep and did receive a service bulletin about this many years ago. I always pull the Blend Air systems whenever I run into them on any unit I service.
63Dream
Posts: 5
Joined: Mon Jan 21, 2013 9:24 am

Can you tell me which wires I need to disconnect?
DaleM
Posts: 385
Joined: Wed Apr 07, 2010 10:07 am

There will be a red, white, green and yellow wire coming from the Blend Air box. Those are tied into the thermostat wiring. Just remove those from the thermostat wiring.
63Dream
Posts: 5
Joined: Mon Jan 21, 2013 9:24 am

I did disconnect the blend air system and have had no more problems so far so maybe that was the problem. Thanks DaleM and GOD BLESS.