Blower starts, but condensor won't.

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
xr7g428
Posts: 1
Joined: Fri Oct 05, 2012 2:15 am

I have a Coleman Evcon DRHS0601CB heat pump. Intermittently the blower will start, but the condensor unit won't. The contactor clicks about every 30 seconds but won't hold. I have 24 volts going to the control board. Coming out of the control board I am getting about 12 volts. When the contactor clicks the voltage spikes upward momentarily. I have recently replaced the start run cap the condensor fan motor and the contactor. Do I need a new control board.

Please do not tell me to call a pro. They came out an told me that I needed to replace the unit. They didn't even take the panel off to look at it. They "added" freon and charged me over $500. The pros around here are crooks.