About 2 min after cooling starts the fan relay goes off/on about 7 times then runs fine for the rest of the cycle. I have changed tstat/ wire/ board/ comp contactor. Have 26 v from xformer. If I disconnect yellow wire to contactor fan runs fine.
db
DGAT blower goes off/on 7 times
I assumed that because the blower starts and runs for about 2 min and then will run for a long time after the on/off thing that the cap IS GOOD. The relay on the board goes off and on and again I assume the relay is turning the blower off and on. Also, this issue ONLY happens when the outside contactor is engaged. However, I will try the cap because I'm out off ideas. Thanks for your input. Just talking about the issue helps me try to understand it.
-
- Similar Topics
- Replies
- Views
- Last post
-
-
DGAT Series furnace air-conditioning issue
by minnie1967 » Thu Jul 13, 2017 9:48 am » in Coleman Service & Repair - 0 Replies
- 47424 Views
-
Last post by minnie1967
Thu Jul 13, 2017 9:48 am
-
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 38600 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 98975 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 141434 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
- 1 Replies
- 33776 Views
-
Last post by Greg
Sat Jan 06, 2018 9:11 am