Presidential II 7655 blower won't turn off

Questions about repairs and parts for Coleman furnaces, air conditioners and heat pumps for manufactured homes. Click here for Coleman parts.

Moderators: Greg, Mark

Locked
donuts1a
Posts: 5
Joined: Mon Feb 16, 2009 11:41 am

Have 84 Skyline with Presidential II 7655-856 gas furnace problems - replaced blower and capacitor, then thermocouple. After replacing thermocouple blower won't shut off so have to do it manually. Was told it might be sequencer, but don't know where it is or what it looks like.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

Your furnace does not have a sequencer. The fan switch controls the blower motor operation.


Fan Switch # 7975 - 3281 can be seen and ordered from here by paging down :

http://www.aberdeenhomerepair.com/store ... -7975-3281



Could also be a shorted wire somewhere.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
donuts1a
Posts: 5
Joined: Mon Feb 16, 2009 11:41 am

Changed bottom switch, blower still won't shut off. There is a similar looking switch at top, could it need replacing? Including photo.
You do not have the required permissions to view the files attached to this post.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

One is a limit and the other is the fan switch which I gave ordering info on.




Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
donuts1a
Posts: 5
Joined: Mon Feb 16, 2009 11:41 am

That did it. Thank you very much sir.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

You're very welcome, happy to help.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?